Author Topic: Belly Tank Build Diary  (Read 367413 times)
Offline Mike Brown
Re: Belly Tank Build Diary
« Reply #420 on: January 12, 2020, 04:43:06 PM »
I designed and built a small circuit for the linear heat detection system.  There is a green LED to signal that everything is working.  If the cable becomes disconnected a yellow trouble LED illuminates.  A photo of the prototype board is attached.
Offline Mike Brown
« Reply #421 on: January 12, 2020, 04:47:47 PM »
If a fire is detected the red LED illuminates.  I used a heat gun to test the system on the bench.  My plans are to make this into a very compact system that just requires 12-16Vdc a terminal barrier to attach the cable and LEDs on the end.  It will add some peace of mind to know that there is a fire detection system in the engine compartment.
« Reply #422 on: January 12, 2020, 05:57:35 PM »
Mike, do you have any data on your linear heat sensor?
« Reply #423 on: January 12, 2020, 06:59:03 PM »
That is impressive that you can figure out how to make something like that.  Are you an electrical engineer?
« Reply #424 on: January 12, 2020, 09:46:39 PM »
Or maybe stayed in a Holiday Inn recently  :naughty  :cheers:
Offline Mike Brown
« Reply #425 on: January 13, 2020, 10:27:48 AM »
I am not an electrical engineer but have been designing equipment including electronic circuits for almost my entire life.  No college education, just four years in the Marine Corps.
Offline Mike Brown
« Reply #426 on: January 13, 2020, 10:29:11 AM »
Please find attached information on the linear heat detector cable.
« Reply #427 on: January 13, 2020, 10:59:15 AM »
I'm guessing you chose the 356 degree wire for the car.
Cool idea....  :clap
Always good to hear that people continue to use their military training... Lots of us out there that learned how to do stuff without going to college...  :?
« Reply #428 on: January 13, 2020, 11:07:16 AM »
Thanks for the info, Mike. That is interesting stuff but I wonder why Kidde doesn't specify the min/max specs for its "open" and "shorted" resistance?
Offline Mike Brown
« Reply #429 on: January 13, 2020, 12:25:29 PM »
Neil,
The open resistance is almost infinite, my meter goes to 15 meg-ohm and it registered open.  In the shorted condition it is very shorted, like ohms.  Most fire alarm applications use 4 kili-ohm to 50 kili-ohm end of line resistors for supervision.  Loop current is limited to a few milliamps so that the fire detection system can't actually start a fire.  The conductors are tinned but "wetting current" is still a consideration along with the maximum current the shorted cable would be able to handle.  That is why I prefer to use an opamp circuit like most fire alarm panels to detect the change in state of the cable.  It was just easier to build a little circuit rather than try to fit a fire alarm panel inside a belly tank that has no extra space.
« Reply #430 on: January 13, 2020, 04:39:31 PM »
That makes sense, Mike. I wonder why Kidde did not include that spec in their data sheet.
I applaud your use of op amps in your circuit!  1drink (I used to work for Burr-Brown & then Texas Instruments when they bought BB). Let me know if you need any design help with op amp or instrumentation amplifier circuits.
Offline Jack Gifford
« Reply #431 on: January 14, 2020, 01:37:48 AM »
... If the cable becomes disconnected a yellow trouble LED illuminates...
So- you monitor the far end and recognize an open circuit?
What constitutes "everything" to illuminate the green lamp?
« Last Edit: January 14, 2020, 01:39:49 AM by Jack Gifford »
Offline Mike Brown
« Reply #432 on: January 14, 2020, 07:41:37 AM »
The green LED indicates that the circuit is powered up with no "trouble" on the detection circuit.
« Reply #433 on: January 14, 2020, 10:56:00 AM »
Jack;
The 50k resistor is across the end of the twisted pair so that the circuit knows that the wire isn't broken, which would read as an open circuit.
« Reply #434 on: January 15, 2020, 01:17:10 AM »
Thanks Neil.