I have two pinion direct drive over drive units (4WD) that are clutch packs applied by CO2 pressure through pressure drop switches to solenoids. I have a double redundant electrical system from the shifter & I installed some small LED lights to be able to quick check that both systems are working before a run. When I shift it, the LED's only flash one time when that circuit is powered up although the power is still on. If I disconnect then reconnect the light while the circuit is still powered up, the light will stay on.
The ground for these lights is through a ground switch so theoretically they would only come on by activating that switch to test but the lights actually have a less intense flash with no ground activated at all!
Is it due to a voltage surge by the solenoid?
Is there a way to fix this other than changing to incandescent lights?
Sid.
Sid,
I suspect that you are having problems with back EMF. Large solenoids generate large currents when activated and deactivated. It is always preferrable to have a substantial diode connected reverse polarity across the solenoid as close to the solenoid as practical. There could be a myriad of issues if you could supply a schematic of what you are doing it would help.
Mike, you have the answer to my question.
I was so disgusted with it last night I had to walk away to keep my composure.
What it's actually doing as I relook at it today, the lights don't do anything when the solenoid is activated, they flash when the solenoid is deactivated.
I'm just going to back to the 20th century where I belong & put some real lights on it.
Sid.